Search the forum,

Discuss Burnt Main Downstream Neutral in the UK Electrical Forum area at ElectriciansForums.net

Only the lower heater should be connected in a two immersion heater cylinder if no off-peak/E7 supply is available.
The upper heater is only there to be a boost element in an off-peak/E7 setup. It will do little to no work if it is switched on at the same time as the lower heater, the heat from the lower heater will quite quickly operate the thermostat of the upper heater and switch it off. Also with modern immersion heaters the lower element can operate the overheat trip of the upper element and switch it off permanently (until reset)

Why are you quoting the 230V power ratings? The public electricity supply in the U.K. is 240V, the mythical 230V only exists on paper and not in the real world. These immersion are will be operating at 3kW and using the lower power ratings will lead to you designing and installing a circuit with a small overload which is a dangerous situation.

What is a rubbish/null IR reading? All of the IR testers I have used have only ever had a numerical scale so I haven't a clue what those readings equate to.
He's probably using 230 v because that is what we are taught to use from college and bs7671.
We are required to record the nominal voltage on our test certificates as 230 volts and not the measured value.
Also voltage drop calculations are based on 230 volts it's 3% of lighting etc based on 230 volts yes it takes the worst case scenario.
Maximum zs values calculations require it to be 230 x 0.95.
Where I do agree that most of the time the voltage is around 240-245 volts it's not the voltage we are told to use maybe common sense tells us different.
Maybe it's not 'the real world' but it is whAt it is.
 
latest one being corbyn's u turn on student fees. promise.. we'll scrap them.. now you students have voted labour, we wouldn't.
 
Typical....someone mentions a relatively minor point* about Voltage (each immersion carried a plate stating 230v...not because that's what I was taught at college - thanks all) and the thread goes way off into Labour party election promises...

The IR readings for the Ring Final returned 0 and 5.5 and 5 MegOhms (must I state that these were for readings through L-E, L-N and N-E...?) and c.350 MOhms or thereabouts for the other circuits - 6A lighting and 2 No. 32A Radial (yes, I know a 32A on a radial is unusual). Either way, they're rubbish so that's why I assumed (wrongly) that you'd all be able to assume I knew what was a good, reasonable, unacceptable and utterly rubbish reading.

*Please - do not start arguing the ---- - of course Voltage is a critical element of everything we do - I mean minor as in the relevance to the problem - low/no IR readings.
 
Are you saying the IR reading between Live and Earth on the RFC was zero ohms ??
 
He's probably using 230 v because that is what we are taught to use from college and bs7671.
We are required to record the nominal voltage on our test certificates as 230 volts and not the measured value.
Also voltage drop calculations are based on 230 volts it's 3% of lighting etc based on 230 volts yes it takes the worst case scenario.
Maximum zs values calculations require it to be 230 x 0.95.
Where I do agree that most of the time the voltage is around 240-245 volts it's not the voltage we are told to use maybe common sense tells us different.
Maybe it's not 'the real world' but it is whAt it is.

We are given 230V as the nominal voltage yes, but that is nominal.
Nothing in the regulations tells us that it must be used to calculate current ratings, as far as I know the regulations don't tell us anything about how to calculate current.
The regulations do state at various points that nominal values should be used when no better information is available, the actual voltage is always readily available to us.

The regulations do however require that we do not allow small overloads to be designed in to a circuit.
Designing a circuit based on 230V power ratings when the actual voltage is higher will lead to such small overloads being designed in to the circuit, which is dangerous as the ocpd will not operate on such overloads.
 

Reply to Burnt Main Downstream Neutral in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
681
This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
1K
I'm having an extension built and the builder leading the project has said that the electrician will be over in about 4-6 weeks to start his works...
Replies
4
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock