I had an EICR certificate done recently and it came back with a C2 for RDC protection on the freezer socket (as below). A picture of the consumer unit is also below. The question I had is what do I need to do to fix it, what is the easiest solution? Does this require the circuit breaker to be switched out with an RDC - can be this done here? Can you use a pluggable RDC unit instead of changing the consumer unit, would that be compliant?

Thanks in advance for any comments.

SS1.png

CU1.png
 
There are different ways of providing RCD protection for the freezer socket. Perhaps the simplest and cheapest would be to take the cable out of the MCB and wire it into the ground floor sockets MCB as a spur at the origin of the circuit (which is RCD protected).

Another way would be, as you say, to replace the freezer MCB with an RCBO (which combines the functions of the MCB with an RCD), which should be available for this type and make of consumer unit.

The absolute best way for many reasons would be to change the whole consumer unit for one that contains an RCBO for each individual circuit, though this works out quite a lot more dosh.

Whichever of these methods, or any other, is chosen, the work should only be done by an electrician as there are safety implications involved, such as testing the RCDs etc.

Some may argue that the C2 for a fridge socket should only be a C3, improvement recommended.
 
Last edited:
Perhaps the simplest and cheapest would be to take the cable out of the MCB and wire it into the ground floor sockets MCB as a spur at the origin of the circuit (which is RCD protected).
Not forgetting to move the neutral into the separate neutral bar, also connected to rcd.

And the earth wire too. Make sure they’re all in matching terminal numbers.


Why would note 2 only attract a C3 when note 4 is C2? The problem is still no RCD when there should be one. C3 for both.
 
Late to the party, but DEFINITELY a C3.
If you want to change it, it should be a simple job to move the RCD to 8 and 9, and slip the freezer MCB in at 10.
I wouldn't recommend a freezer on its own RCD (or use a RCBO) because the first you'll know that it's tripped is when you discover that everything is thawed. Share with the telly, and you'll know in time.
Does your cooker isolator in the kitchen have 13A socket built into it?
 
Personally I think it's a C3 however you could change the freezer socket to a RCD socket might need a spacer or two as RCD sockets are quite deep
 
Wouldnt comply surely? SRCDs to BS7288 don't comply with additional protection requirements due to internal clearances.
I think the general consensus, the last 300 times we did this, was that the omission of BS7288 was an omission to be amended at the next amendment.

But I'm all for 301 if anyone fancies it?
 
I think the general consensus, the last 300 times we did this, was that the omission of BS7288 was an omission to be amended at the next amendment.

But I'm all for 301 if anyone fancies it?
I'll take 301 ?

The IET did have the following publicised

Are S-RCDs and FCU-RCDs (to BS 7288) recognised for additional protection in BS 7671?
RCDs to BS 7288 are not recognised for use as an RCD by BS 7671:2018. See Regulation Group 531.3.4.

Clause 1 of BS 7288:2016 states “SRCDs are intended for use in circuits where the fault protection and additional protection are already assured upstream of the SRCD.”

Further, Clause 0 of BS 7288:2018 states the devices are only suitable for additional protection against direct contact, and therefore cannot provide fault protection (e.g. where disconnection times cannot be met in a circuit), nor would they be recognised for additional protection against fire due to short circuits in appliances or flexible cables connected to the socket-outlet or connection unit.

However, there is nothing to stop accessories containing SRCDs to BS 7288 being fitted in electrical installations complying with BS 7671, as they comply with the relevant standards, although as stated the RCDs within them cannot be recognised for the functions of fault protection or additional protection for the purses of BS 7671.
Source; https://electrical.------.org/bs-7671/faqs/qa-from-rcds-selection-types-and-testing-webinar/
 
Interesting. So it would seem Connections may have got it wrong.
I must admit I had wondered why, if it was a mistaken omission, that it wasn't corrected in the corrigendum.
So in light of this, there would seem to be little point in using such devices, as there would have to be additional protection upstream anyway.
And yet they're still being manufactured and sold.

Me no understand!
 
Well, it would appear 301 is on.

That statement is expectedly wooly however. It explcitly rules out additional protection against fire and also fault protection but not against additional protection against electric shock, if I'm correct in translating "direct contact" to mean electric shock.

I'd take from that they are ok to meet the requirements of additional protection against electric shock.
 
This is NOT a C2. The Zs to the socket is what's important, and it probably complies with disconnection times anyway. Original installers Common sense has prevailed here, the clue is in FREEZER socket. Providing adequate earthing is in place a code 3 for an rcd socket install maybe ?? but that's about it. Trouble is, its his call because he has signed the report.
 

Reply to C2 on EICR due to RCD Protection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K
Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Replies
15
Views
1K
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
6K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
89
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock