Hi All,

I have been searching the forum but can't find this anywhere. Can you please see if my interpretation of this is correct:

50x50 trunking, 2m run with 1 90[SUP]o[/SUP] bend.
4 x 50mm conductors,
1 x 35mm conductor.

As there are no factors for over 25mm[SUP]2[/SUP] I have to work it out manually

50x50 = 2500mm[SUP]2[/SUP] (total space)
-
4x50 = 200mm[SUP]2[/SUP]
1x35 = 35mm[SUP]2[/SUP]
Total 235mm[SUP]2[/SUP] which is less than 45% of the trunking capacity, therefore 50x50 is compliant?

Thanks for your help,
(this is my first post :))
 
Hi Chris
I am using IET On Site Guide green book for reference and as you already know Table E5 goes up to cable size 25 mm sq. and Table E6 is for the trunking sizes. However the rest of the page under table E6 states what to do for cable sizes not tabulated in TableE5 (too long to type out here). It seems you are calculating correctly provided you are using the internal csa of the trunking, and keeping to 45% space factor, and assuming you are not breaking any rules for minimum internal bend radius ( Table D5) And as this is your first post, this is my first reply. Have fun
John
 
two things spring to mind, one is insulation, and the other is how to get them around the 90 degree bend. Some cables are better than others for this and some go to 90C which can help if you are having some issues with load.
 
i take it the op is for some design project or something?
cos in real life the 50mm tails will be hanging out of the 90 degree bend by some distance.
 
Hi All,

I have been searching the forum but can't find this anywhere. Can you please see if my interpretation of this is correct:

50x50 trunking, 2m run with 1 90[SUP]o[/SUP] bend.
4 x 50mm conductors,
1 x 35mm conductor.

As there are no factors for over 25mm[SUP]2[/SUP] I have to work it out manually

50x50 = 2500mm[SUP]2[/SUP] (total space)
-
4x50 = 200mm[SUP]2[/SUP]
1x35 = 35mm[SUP]2[/SUP]
Total 235mm[SUP]2[/SUP] which is less than 45% of the trunking capacity, therefore 50x50 is compliant?

Thanks for your help,
(this is my first post :))

From my Trunking and Cable Data:

Trunking Factor for 50 x 50 One Bend = 1037
Cable Factor for 35mm[SUP]2[/SUP] = 95
Cable Factor for 50mm[SUP]2[/SUP] = 132.7

(4 x 50mm[SUP]2[/SUP]) + (35mm[SUP]2[/SUP])= a Combined Cable Factor of 548.8 + 95 = 643.8 which is less than the Trunking Capacity of 1037 and so complies.
 
Last edited by a moderator:
Thanks all for your replies.

Yeah it's for a design project but I hadn't taken into consideration whether the conductors would fit in the bend. My naivety of the physical size of the cable assumed it would.
MarkieSparkie I would too be interested to find out the source of your cable factors please?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Cable factors in trunking, conductors over 25mm^2.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
chrislee765,
Last reply from
chrislee765,
Replies
6
Views
8,031

Advert

Back
Top