But not better than an old Avo!You could do away with the timer and install a hive reciever in the area where the zone valves are.
A 2 channel hive (or similar) would work and leave you an extra core if needed as the hive only needs a 230V supply
You would still be able to connect things to this such as remote thermostats etc.
How would that solve the problem?
Unless I am reading it wrong there is one core short at the junction box (where the zone valves / cylinder are)
The Hive (or similar) only needs a L,N,E so the reciever can be located adjacent to the joint box. As the reciever will give you seperate switched lives for HW (on), CH (on) and even HW (off) if you need it in the cylinder cupboard you will have a supply and switch wires needed at that location.
Am I missing something?
I would have the 4 cores asYes there are 4 cores between the joint box and the boiler when it requires 5, so the pump cannot currently be connected to the pump terminal of the boiler.
The controls, whether they are wired or wireless have no bearing on this part of the circuit.
I was assuming the 5 cores went from the boiler (FCU) to the cyliner cupboard.But if the receiver is in the cupboard, the problem is getting its output to the boiler.
I would have the 4 cores as
L,N,E - supply to JB (install hive reciever at joint box)
4th core pump over run