They linked to the CEF site which says nothing about the manufacturer.
However, I do happen to have a short bit of the non-LSF version of that cable from CEF and it says on the side "EL SEWEDY CABLES" which I think are an Egyptian manufacturer.
It is interesting that the neutral is one showing the melting action after what Julie just posted!
They all look a bit overheated to me though.
Given the marginal rating anyway (154A clipped direct from table 4E4A) and the fact this is possibly a non-linear load, you should really look at replacing it with something heavier.
50mm is the next obvious thing but depending on the results of checking for harmonic currents it might be a case of looking at 70mm, and check before that the various connectors are able to take that size (they ought to, but just in case...)
It might also be worth going to a supplier like Yesss that do a brand like Doncaster Cables with a known reputation, as the small price difference over CEF's best-price choice is nothing compared to the time and effort being wasted on problems!
[automerge]1590512969[/automerge]
Check though as cable-wrangling with 70mm is going to be a lot harder and typically they have sector-shaped conductors.
You should be limiting your maximum cable temperature to 70 degrees thus the ccc will decrease, unless it is ascertained that the Switchgear that the cable it is terminating to is suitable for 90 degrees, which in most cases is no.Hi,
When choosing a cable, you should focus on the installation conditions. Derating factors can significantly change the base value of current carrying capacity. Are there any loaded neighboring cables or communications?
In any case, initially the cable was selected at the limit, without current margin. Next is your case without correction factors:
View attachment 59020
and the report ….
View attachment 59021
Can you clarify the installation conditions and the effect of the loaded neighboring cables?