Discuss Cable ratings - constant load? in the UK Electrical Forum area at ElectriciansForums.net

Hi,
When choosing a cable, you should focus on the installation conditions. Derating factors can significantly change the base value of current carrying capacity. Are there any loaded neighboring cables or communications?

In any case, initially the cable was selected at the limit, without current margin. Next is your case without correction factors:
View attachment 59020
and the report ….
View attachment 59021
Can you clarify the installation conditions and the effect of the loaded neighboring cables?
You should be limiting your maximum cable temperature to 70 degrees thus the ccc will decrease, unless it is ascertained that the Switchgear that the cable it is terminating to is suitable for 90 degrees, which in most cases is no.
 
If we limit the maximum cable temperature to 70C degrees, then the current carrying capacity of the cable Cu 35 mm2 is 119 A only (with the C-installation method).
1593113653425.png

To supply a load of 150A per phase, then you need to use a cable Cu 70mm2 (this will be with a small margin).
1593113700274.png
 

Reply to Cable ratings - constant load? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
405
In show world we use 19c 'socapex' cable as a staple, standard cable for connecting lighting dimmers to lights via 19 pin screwed connectors and...
Replies
3
Views
1K
Apologies for the complexity of this question, but there’s no easy way to explain it. This is a remote Norfolk house and workshops, developed...
Replies
12
Views
2K
with a single UPS rated at 8KVA, 230v, stating maximum input current of 44A, would the over current device, cable size etc be based on the 8KVA...
Replies
2
Views
2K
Argument at work! on an EICR its common to find a 9.5kW shower wired in 6.0mm T/E with a 40 amp MCB. obviously a code 2 unless short run and...
Replies
75
Views
18K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock