I've been away and haven't had a chance to post an update but I have made changes.
The 2.5 radial is now on a 16A MCB.
Cables entering the CU are 1 circuit per grommet with no visible gap between the cable outer sheath and the grommet membrane.
Tails and earth cables are retained with metal banding. The service head, meter and CU are to be enclosed in a cabinet which has always been the plan.
The cables running up the wall in the trunking were already also retained with metal banding screwed to the wall at intervals not exceeding 400mm, which is also the method of retention in the walls before being plastered over.
Also checked the main fuse rating is 60A as I recalled.
The 2.5 radial is now on a 16A MCB.