Hi all, I was asked in the office last night what size cable would be required for a 12V 1000W windlass with a cable length of 14m. I know how to calculate but where do you find the tables for 12V volt drop etc?
 
you're going to need one hell of a big cable. use resistance per metre from tables, multiply by 14, then V=IR, where I=83A
 
going to need at least 50mm cable. don'tforget, the warme the cable gets, the higher the resistance and hence increased VD.
 
Hi,it is a pretty standard install. Use 50mm high quality welding cable,and get someone to sort the runs and containment,correctly.
Long runs of multi-stranded flexible,can be very hygroscopic,and will need correct attention,at terminations.

Make sure the installer understands the word "hygroscopic"....as the yankee spell-check,has failed :rolleyes:
 
Hi all, I was asked in the office last night what size cable would be required for a 12V 1000W windlass with a cable length of 14m. I know how to calculate but where do you find the tables for 12V volt drop etc?

It's the same volt drop table as any other voltage, the resistance of the cable doesn't change.
 
Other details,i forgot to add,were it's duty ratings. It's not a bow-thruster,so it will have short duty-cycles (all in the MI) and 1000W is the maximum,so majority of use will be way below,at no-load operation.

Anchor winch,would be a whole different basket of whelks...
 
Well,i suppose it's all relative....

It's forecast a change,to 10,and you need to do a rake of furling and unfurling,to get back to safe waters....

The cable,is an average length of site,MMA welding cable....

I wonder which job,is the one where you thought "Mmmm,i'm glad i spent that money..." :)
 
Just the job for me indeed...provided it's Capstan Full Strength!
However, just for clarification, is this an anchor windlass or a furler we're talking about? Clearly, the Lofrans linked to above is the former...
 

Reply to Cable selection on boat for 1000W motor in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, thanks for reading this. Ive been asked to look at a job where the DNO connection (single phase 80A TT) is a long run to the final circuits...
Replies
4
Views
247
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
598
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
752
Hi everyone, I'm looking to do some cable runs for cat6 etc in my house and was looking for some advice on blind wiring. I'm not skilled but I...
Replies
0
Views
785
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
824

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock