wee jock

A customer has bought a Rangemaster cooker 14.8kw, Rangemaster state the FLC is 55amps, cable wiring ref method is 100.............what cable breaker size should I use. This is for a domestic property?
 
start by applying diversity. this should give you around 25A as a ccc for the cable.
 
You need to factor in diversity here as it's a cooking appliance and will never get anywhere near the manufacturers rating.
 
Done diversity using the Kws / v, I'm really looking for someone to confirm what I have in my head or if I'm just mad!
 
6mm cable on a 32A MCB, unless you want to got to 10mm on a 50A. it's your call. client's brass.
 
In theory the cooker amps would be 14.8kw / 230v this gives 64.5amps, I've seen on another forum it's full load operating current is 55amps measured at the cooker. So if any of you nice guys out there who do a bit of design I'd greatly appreciate it.
 
Everything I'm looking at is pointing to 16mm using online cable calculators & iPhone apps. Can't see a 6mm cable taking 55amps! Just saying, that's why I'm asking
 
what the lad are trying to say is that in reality the cooker will never take 55A. all of ther heating elements are controlled by thermostats, and because of that, they will be turning on and off as required. The max Kw rating will be calculated from ading the rating of all of the elements and fans together. This will rarely if ever happen.
read the OSG, page 109 onwards
 
Johnboy, I understand that and I believe that's why the cooker takes 55 amps and not 65 amps as 14.9kw / 230. Calculate diversity on the 65amps gives you 26.5amps. When I put all the above info into cable calcs, FLC 55, design current 26.5amps, install method 100 keeps telling me 16mm!
 
Missed out that it's an induction hob, the hob itself is 7.8kw!
 
Last edited by a moderator:
Need to ask the computer that.
Been told you can't apply diversity for induction hobs as the manufacturer has already applied this!
By applying diversity to give you 26.5 amp this is the design current?
 
Johnboy, I understand that and I believe that's why the cooker takes 55 amps and not 65 amps as 14.9kw / 230. Calculate diversity on the 65amps gives you 26.5amps. When I put all the above info into cable calcs, FLC 55, design current 26.5amps, install method 100 keeps telling me 16mm! 

well either your sums or your software calcs are going wrong somewhere.
i calculate the load to be 28amps after diversity and without a socket in the cooker switch.
so , In => Ib thus your mcb will be 32A.
 
The hob takes 33amps itself diversity applied, the ovens & grill take 16 amps diversity applied. So total current is 49 amps!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cable Size
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
wee jock,
Last reply from
Chr!s,
Replies
22
Views
7,021

Advert

Back
Top