bogney
Unconventional column 6...?
Because of the use of 2 core? The OP is suggesting this with the 4 core in parallel.Unconventional column 6...?
I assume you are doubling Column 6 from Table 4D4A to get 92A, problem is it ain't a 2 core cable?Your CCC would be 92A and your pump house perhaps a maximum of 50A so that would leave you 40A to divide among the caravans.
However your volt drop will be well beyond limits at that loading, especially as you want to extend further for the caravans.
I have just checked and I think you would need to keep your current below about 6A to keep within 6.9V (3%) drop over 300m with a 12mm² cable!.![]()
Yes I was doubling the tabulated CCC as recommended when using cables in parallel, however the regulations are thinking of two separate two core cables suitably arranged to ensure equal current sharing, which may well not be the case here, I agree.I assume you are doubling Column 6 from Table 4D4A to get 92A, problem is it ain't a 2 core cable?
Not calculated the volt drop but under maximum loading I don't doubt it will exceed requirements.Yes I was doubling the tabulated CCC as recommended when using cables in parallel, however the regulations are thinking of two separate two core cables suitably arranged to ensure equal current sharing, which may well not be the case here, I agree.
However this is moot since the VD is something in the region of 50V!
My view that cable if PVC insulated will be rated at 76A, if XLPE then 88A.
This is such a common mistake I see, you may well know this so it could just be for the benefit of others.
XLPE only has a higher current rating if everything it's connected to is also rated to operate at 90 deg C. If it isn't it's CCC is reduced to that of a PVC cable.
Yeah know this, that however is the maximum rating of the cable where conditions satisfy.This is such a common mistake I see, you may well know this so it could just be for the benefit of others.
XLPE only has a higher current rating if everything it's connected to is also rated to operate at 90 deg C. If it isn't it's CCC is reduced to that of a PVC cable.