Screenshot_20210104_092558_com.whatsapp.jpg
 
It will fit into the space outlined in orange, but there are other considerations. what will it be used to power, and does the curcuit require RCD protection?als bear in mind that it should be same make and type as existing.
 
It will fit into the space outlined in orange, but there are other considerations. what will it be used to power, and does the curcuit require RCD protection?als bear in mind that it should be same make and type as existing.
Hi thank you yeah it's the same make and it's for electric shower I was concerned that the 80a RCD already has 70a worth of switches next to it already or is it possible to but the 50a alongside them
 
What's the kW rating of the shower? and bear in mind that the 3 other breakers' values are max. rating. the actual load willbe much less most of the time.
 
you'd just get away with 6mm cable on a 40A MCB if no insulation on the cable route. but if installing the cable go for 10mm on a 50A.
 
OK.part p is a building reg. whereby certain works need to be notified to building control at local council. any work within a special location (bathroom) falls under this. your guy will need to be a member of NICEIC or one of the other similar organisations.
 
If you have a new Wylex MCB don't assume it will fit the NSB range hasn't been manufactured for a good number of years
Wylex told me I had to replace all the breakers in their CU when we ran a new circuit for a cooker range - 2020, because the existing were BSBs.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Durham Uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Can a 50a MCB be fitted into that space ?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
Dannythehitman,
Last reply from
richy3333,
Replies
15
Views
2,834

Advert

Back
Top