Dannythehitman
- Reaction score
- 3
Discuss Can a 50a MCB be fitted into that space ? in the UK Electrical Forum area at ElectriciansForums.net
Hi thank you yeah it's the same make and it's for electric shower I was concerned that the 80a RCD already has 70a worth of switches next to it already or is it possible to but the 50a alongside themIt will fit into the space outlined in orange, but there are other considerations. what will it be used to power, and does the curcuit require RCD protection?als bear in mind that it should be same make and type as existing.
It's a 10.5kw thank you for all of your adviceWhat's the kW rating of the shower? and bear in mind that the 3 other breakers' values are max. rating. the actual load willbe much less most of the time.
10mm cable?It's a 10.5kw thank you for all of your advice
Sorry 9.5 kwIt's a 10.5kw thank you for all of your advice
Hi I have done 10mm to 50a double pole switch directly one cable then from switch to shower 10mm one cable and then looking to fit 50a weylex breaker in that spaceyou'd just get away with 6mm cable on a 40A MCB if no insulation on the cable route. but if installing the cable go for 10mm on a 50A.
looks OK. but wot about part pee?Hi I have done 10mm to 50a double pole switch directly one cable then from switch to shower 10mm one cable and then looking to fit 50a weylex breaker in that space
Sorry for ignorance what is thatlooks OK. but wot about part pee?
I have looked and have a guy to sign it off once work completedSorry for ignorance what is that
If you have a new Wylex MCB don't assume it will fit the NSB range hasn't been manufactured for a good number of yearsHi thank you yeah it's the same make and it's for electric shower I was concerned that the 80a RCD already has 70a worth of switches next to it already or is it possible to but the 50a alongside them
Wylex told me I had to replace all the breakers in their CU when we ran a new circuit for a cooker range - 2020, because the existing were BSBs.If you have a new Wylex MCB don't assume it will fit the NSB range hasn't been manufactured for a good number of years
Reply to Can a 50a MCB be fitted into that space ? in the UK Electrical Forum area at ElectriciansForums.net