J
Jon Bridges
Hi, I'm about to put some 1.5 3-core SWA on an outside wall for a lighting circuit. The customer wants me to run it next to all his Virgin TV Coax (about 6 cables). Will my SWA cause interference or will the steel prevent this?
JB
Good question.
I would say it would be fine as the steel of the SWA will provide a fair bit of 'insulation'.
co ax is screened anyway to prevent interference or "noise" to use the correct term. however if possible connect the steel wire to ground at your terminations and you are effectively screening your SWA cable also.
The SWA probably acts as a good faraday cage. saying that the armored strands would have to criss cross.
Careful there, are you all sure that the armouring will comply with the necessary & required segregation of band1 iT circuits usually recommended as 300mm if no barrier present... I'm not saying it won't but I would check that Satellite cable insulation is rated for 230v ac at least.
You beat me to it. I doubt whether coaxial would be rated for low voltage applications and as such would have to be suitably segregated.
Have a look on page 62 of the OSG Notes section below table 7.7 and the table itself should shed some light maybe.
I have seen 50 + coaxes (for CCTV system) running on the same trapeze bracket with YY cables (on e layer above anothe and sometime side by side) there were no ill effects on the picture quality