whitebeetle

Hi All , Got to move the consumer unit for a friend , i believe the furthest it can be moved from the meter is 3 metres but can i bury the double insulated meter tails in the wall or do they need to be uncovered or in trunking. If they can be buried , what protection is needed ?


Many thanks
Chris
 
Yes you can but then your going to have to go down the road of providing RCD protection for them if you do not apply additional protection as per Rergulation 522.6.6.
 
Thanks for your help , much appreciated. If i cover them in Galvanised trunking would that be adequate without rcd protection ? Perhaps surface mount would be better ?
Chris
 
You would have the hassle of earthing that trunking if the trunking, which I would imagine it is, is to BS 50085.

Unless there is a real aesthetic reason you need to bury it, then surface is going to be the only reasonable method of erection
 
You could:
conceal the cables at a depth greater than 50mm,
use a cable with an earthed metalic sheath (such as SWA),
use earthed trunking or conduit,
provide mechanical protection sufficient to prevent the cables being penetrated by screws or nails (doesn't have to be earthed),
install the cables in a safe zone and provide 30mA RCD protection (not time delayed).
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Can meter tails be buried in the wall ?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
whitebeetle,
Last reply from
Welchyboy,
Replies
6
Views
14,309

Advert

Back
Top