Discuss Can't figure ring final r1 + r2 divided by 4 in the UK Electrical Forum area at ElectriciansForums.net
Hi...keen amateur here......don't crucify me for asking!! I understand Ohm's law and I understand the mechanics of measuring end to end on ring final and then joining incoming live to outgoing neutral etc, and I know that this configuration gives a figure of 8 (in fact can be straightened to give a complete circle) but I can't figure out the "calculated method" of dividing by (r1+r2)/4....why?
If you meter across the mid point of the "circle" then yes...
if K= r1+r2 (the complete circle) then...since in parallel...
1/R = 1/(K/2) + 1/(K/2) which simplifies to 1/R = 4/k, then R=K/4....(r1+r2)/4........but what happens if you measure across the circle at any other point other than the mid point?
Far to difficult for a Sunday Afternoon
Ring main cabled in parallel,so the csa of the cable is half & the resistance of the cable is half.
So 1/2 x 1/2 = 1/4.
So we divide by 4 to get r1 & r2.
So 1/2 x 1/2 = 1/4.
R1+R2 to be pedantic again. But then again if we don't get the basics right we get all confused.
To the furthest point or mid point 2 cables are run and the length of cable to the furthest point is half the length of cable in the ring giving a multiplier of 4 for the installed length of cable.
I just think of it as to mid points and 2 cables in parallel = multiplier of 4
Ring Fimal Circuits are basically two sets of conductors wired in parallel.
If you measure r1 + r2, you are in fact measuring two sets of parallel conductors, but in series.
If you had a Radial circuit 50m long and then decided to turn it into an RFC, all you would need to do is run another 50m cable from the Consumer Unit to the last socket.
So although you might use 100m end to end of cable to wire an RFC, the circuit is in fact only 50m long or only 1/2 as long.
Because an RFC is in fact two conductors in parallel, the resistance is halved another 1/2.
Multiply these two 1/2s together and you get 1/4.
Therefore when we measure r1 + r2 in an RFC, we divide by 4 to obtain R1 + R2.
an easy way to simplify it is to consider a length of single cable around 30m of 1.5mm
it's resistance measures at o.36 ohms. now add an identical length in parallel.resistance is halved, so 0.18 ohms
then cut both in half and parallel 2 of the 15m lengths. halved again = 0.9 ohms.
Reply to Can't figure ring final r1 + r2 divided by 4 in the UK Electrical Forum area at ElectriciansForums.net
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
7K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
