Hi there

I have an older Xpelair ceiling fan in the bathroom and have installed a Manrose MF100T but all I have to do now is the wiring, only a bit not install the whole jobby, all I want to know is what wires relate from the old wiring colour scheme to the new wiring colours as I just need to connect via a connector block or Wago etc

Thanks for any help given. :)
 

Attachments

  • 20260430_111828.jpg
    20260430_111828.jpg
    148 KB · Views: 16
  • Screenshot 2026-05-01 at 10-56-57 6243Y Electrical Cable 1mm_1.5mm 3 Core & Earth Domestic Wir...png
    Screenshot 2026-05-01 at 10-56-57 6243Y Electrical Cable 1mm_1.5mm 3 Core & Earth Domestic Wir...png
    140.7 KB · Views: 14
its normally

red - brown
yellow - black
blue - grey

Be aware the red there is likely to be a permanent live.... doesn't go off with the light. The yellow is switched live.... it does go on and off with the light. There might be a 3 pole isolator switch, or isolate the power at the board.

If it doesn't work as expected, swap the red and yellow.... Do NOT swap the blue with anything... that is most definitely the neutral.


For a chack, see if theres markings on the old fan where the cables are terminatied.... Should say PL, SL and N
 
its normally

red - brown
yellow - black
blue - grey

Be aware the red there is likely to be a permanent live.... doesn't go off with the light. The yellow is switched live.... it does go on and off with the light. There might be a 3 pole isolator switch, or isolate the power at the board.

If it doesn't work as expected, swap the red and yellow.... Do NOT swap the blue with anything... that is most definitely the neutral.


For a chack, see if theres markings on the old fan where the cables are terminatied.... Should say PL, SL and N

Hi

Thank you for the kind reply, I will be switching off by the mains just to be sure, I will have a look on the old fan and check the online manual also for PL, SL and N, I take it the earth is not used as it's internally earthed.

Thank you again.
 
Hows my wiring?

I only ask as the unit has LS/N/L which is different from above of PL, SL and N

I await a kind reply

Thank you x

Wiring.jpg
 
Last edited:
This is my interpretation:
PL is Permanent live, which equates to L
SL is switched live, which equates to LS (live switched)
And obviously N is N 👍
 
If you have used black as the neutral, what you've done should work.
But for electricians, for these cable colours, black indicates a live conductor. We are encouraged to use grey for neutral (as Littlespark suggested in his list of colours in post #2)
So the ideal way to do this would be to use grey for neutral, wrapping a small a piece of blue insulation tape around both ends, to avoid doubt.
Ideally you could change it, or if you leave as is, I suggest you put a little blue insulation tape on the black both ends!
Otherwise all good and neat!
 
Last edited:
If you have used black as the neutral, what you've done should work.
But for electricians, for these cable colours, black indicates a live conductor. We are encouraged to use grey for neutral (as Littlespark suggested in his list of colours in post #2)
So the ideal way to do this would be to use grey for neutral, wrapping a small a piece of blue insulation tape around both ends, to avoid doubt.
Ideally you could change it, or if you leave as is, I suggest you put a little blue insulation tape on the black both ends!
Otherwise all good and neat!
Hi I will change the wiring, why couldn’t they just leave stuff alone

And so on my stupid fan PL is just L, (Brown), N is N (Grey), SL is LS (Black) (I'm having a right brain fart lol)

WIRING 2.jpg
 
To answer your question on why can't they leave things alone, it was to do with harmonising the colours over Europe, except in France of course where Red is still the live conductor and Orange is a switched live, Oh and purple is a strapper. 😱
 
Hi. New here so hope it’s ok to briefly piggyback on this thread to show how confusing electrical items can be.
I’m about to start a very similar project to OP, but in my case, the internal wiring for my extractor fan is - as you can see from the photo :
Black - N
Yellow - SL
Orange - L
🤷🏼‍♂️

IMG_6701.jpeg
 
it doesnt matter about the internal wiring colours... they are not dictated by BS7671 which is the FIXED wiring colours quoted earlier in the thread.

Depending how old your house is... from top to bottom on your fan,
N1 is neutral... blue in old colours, grey in new.
SL2 i thing switched live... yellow in old colours, black in new.
And L3 will be the permanent live, Red or brown.

Be wary though, as sometimes in the new colours, the black and grey were swapped...
 
it doesnt matter about the internal wiring colours... they are not dictated by BS7671 which is the FIXED wiring colours quoted earlier in the thread.

Depending how old your house is... from top to bottom on your fan,
N1 is neutral... blue in old colours, grey in new.
SL2 i thing switched live... yellow in old colours, black in new.
And L3 will be the permanent live, Red or brown.

Be wary though, as sometimes in the new colours, the black and grey were swapped...
Thanks for that. No wonder people (myself included) get confused !
My issue is that I don’t have an SL wire going to my existing fan from the isolator (just L & N), so I’m trying to both make access via the loft (insulation and loft boards in a bungalow) in order to access the wires in the first place, but also access a very cramped Knightsbridge isolator switch - which seems to have a lot more wires than I expected.
 
if you link the L and SL, it will work, but only when the light is on.. .there will be no overrun timer...

The fan isolator may have all 3 conductors there... but it sounds like its been used as a joint box if theres a lot of cables
 