I'd go with post #3 consumer unit tightness check. Did the electrician go into the board or just the fittings?
He did everything, the board, the box on the outside of the wall and all fittings. I believe he also checked for voltage fluctuations. Hence he is now suggesting that he will need to life the flooring above to look into it more. How likely is it that we will find something away from the fixtures though? Lifting floors will certainly cause chaos, which I would love to try and avoid.
 
It depends how it's wired. If all joints can be accessed at lights and switches then the problem should be traceable without lifting floors. If joints are in boxes under the floor then these will need to be accessed.
Randomly lifting the floor will not solve anything. A logical approach is required.
 
I'd go with post #3 consumer unit tightness check. Did the electrician go into the board or just the fittings?
He did everything, the board, the box on the outside of the wall and all fittings. I believe he also checked for voltage fluctuations. Hence he is now suggesting that he will need to life the flooring above to look into it more. How likely is it that we will find something away from the fixtures though? Lifting floors will certainly cause chaos, which I would love to try and avoid.

Thanks, we will have to call the pro back in. It might also be worth noting that the white surround of the lamp holders are discouloured brown on this circuit. They have been like it for the year we have lived in the home and have not got any worse, but don't know if this is symptomatic of an issue, or just normal wear and tear.
 
We had our usual electrician in to look at the problem. Of course the lights didn't flicker when he came in, but he did spot check all of the fixtures and said there were no issues. Given that we still have flickering lights i was just keen for advice on whether we should be concerned?
"Usual Electrician" is that a proper Electrician or some Bod that thinks he is an Electrician?
 
He did everything, the board, the box on the outside of the wall and all fittings. I believe he also checked for voltage fluctuations. Hence he is now suggesting that he will need to life the flooring above to look into it more. How likely is it that we will find something away from the fixtures though? Lifting floors will certainly cause chaos, which I would love to try and avoid.
Get a proper qualified Spark in with the correct test gear, and the right approach to fault finding.
 
We had our usual electrician in to look at the problem. Of course the lights didn't flicker when he came in, but he did spot check all of the fixtures and said there were no issues. Given that we still have flickering lights i was just keen for advice on whether we should be concerned?

Did he check the connections in the consumer unit ?, That would have been my first check if you'd called me out and told me that all your lights were flickering.

If as you say the lamp holders are gone brown, then they have been overheated. Possibly by someone using high wattage bulbs in the past or just cheap lamp holders. Easy enough to resolve.
 
Last edited by a moderator:
As mentioned by others get someone decent in and check form the CSU no floorboards should need to be lifted as the cable runs from the CSU to the ceiling rose and to the next one from the ceiling rose to the switch so it should be standard wiring without anything jointed elsewhere.

Unless you live in some Stately home in between St James Park and Victoria......
 