Discuss Certifying remedial including dist board swap. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi,
An easy question if you know the answer.
My house recently failed an eicr done by me.
I've had a couple of jobs I'm fixing (split ring separating into 2 circuits), and some I'm not (no cpc on plastic light switches Upstairs, presumably compliant at time of install. The lights have a cpc as a later addition).
I'm swapping the distboard to full rcbo/metal to give me the room to split the ring to two circuits.
So for the schedule of tests....what needs doing?
Just certify the board/supply?
The above + circuits repaired?
Every connected circuit?
Every connected circuit and two sub dbs with their circuits?
This is going to be notified directly so want to know what should completed?
I'm testing everything, but if I'm completing the full form, then what do I do about the C3?
So for me all the circuits should be on the schedule of test results.
No earth at switches is a C2 unless mitigated by warning notices at consumer unit advising only class 2 equipment to be installed at switches
Strictly speaking no class 1 equipment should be installed on circuit & warning notice at CU advising only class 2 equipment to be used
I'm under the impression that you didn't used to need a CPC on a lighting circuit?
As it was compliant at time of installation, only a c3 is required as a minimum?
It is the crux of the issue. I only want to certify the dist board, not every circuit in the house.
If I put the lights on the schedule of tests am I certifying compliance with current regs (which it does not meet)?
If changing a consumer unit you're certifying the consumer unit.
However, as you've changed the characteristics of every circuit, you also need to test every circuit for continuity of protective conductors at a minimum.
If any circuits would not comply to the extent that a C2 would apply to that circuit, then you must not reconnect that circuit until the C2 has been rectified.
Electrical Safety First has published free guides on how to treat a lighting circuit with no CPC when changing a consumer unit.
All the answers I needed on that thanks!
Complete test sheet, all non-compliances to be listed under 'condition of install' and circuit notes.
Reply to Certifying remedial including dist board swap. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Opinions on this Crabtree TP 10 way board? Got to test this next week after a quick recce on a clients site yesterday. Although probably...
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
