Hi,

An easy question if you know the answer.

My house recently failed an eicr done by me.

I've had a couple of jobs I'm fixing (split ring separating into 2 circuits), and some I'm not (no cpc on plastic light switches Upstairs, presumably compliant at time of install. The lights have a cpc as a later addition).

I'm swapping the distboard to full rcbo/metal to give me the room to split the ring to two circuits.

So for the schedule of tests....what needs doing?

Just certify the board/supply?

The above + circuits repaired?

Every connected circuit?

Every connected circuit and two sub dbs with their circuits?

This is going to be notified directly so want to know what should completed?

I'm testing everything, but if I'm completing the full form, then what do I do about the C3?
 
So for me all the circuits should be on the schedule of test results.
No earth at switches is a C2 unless mitigated by warning notices at consumer unit advising only class 2 equipment to be installed at switches
Strictly speaking no class 1 equipment should be installed on circuit & warning notice at CU advising only class 2 equipment to be used
 
So for me all the circuits should be on the schedule of test results.
No earth at switches is a C2 unless mitigated by warning notices at consumer unit advising only class 2 equipment to be installed at switches
Strictly speaking no class 1 equipment should be installed on circuit & warning notice at CU advising only class 2 equipment to be used
I'm under the impression that you didn't used to need a CPC on a lighting circuit?

As it was compliant at time of installation, only a c3 is required as a minimum?

It is the crux of the issue. I only want to certify the dist board, not every circuit in the house.
If I put the lights on the schedule of tests am I certifying compliance with current regs (which it does not meet)?
 
If changing a consumer unit you're certifying the consumer unit.
However, as you've changed the characteristics of every circuit, you also need to test every circuit for continuity of protective conductors at a minimum.
If any circuits would not comply to the extent that a C2 would apply to that circuit, then you must not reconnect that circuit until the C2 has been rectified.
Electrical Safety First has published free guides on how to treat a lighting circuit with no CPC when changing a consumer unit.
 
If someone removed the white plastic switch and changed it to a nice brass decorative one you would need a cpc.
If you are only certifying the board you still need to include all the circuits in the schedule How far you test them would be in the "Extent of installation covered by this certificate "
 
If changing a consumer unit you're certifying the consumer unit.
However, as you've changed the characteristics of every circuit, you also need to test every circuit for continuity of protective conductors at a minimum.
If any circuits would not comply to the extent that a C2 would apply to that circuit, then you must not reconnect that circuit until the C2 has been rectified.
Electrical Safety First has published free guides on how to treat a lighting circuit with no CPC when changing a consumer unit.
All the answers I needed on that thanks!

Complete test sheet, all non-compliances to be listed under 'condition of install' and circuit notes.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
York
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Certifying remedial including dist board swap.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
Inteificio,
Last reply from
Inteificio,
Replies
9
Views
1,147

Advert

Back
Top