M
marples_matthew
Can I change a C.U without having to re-wire entire house. What about cables runs that we can't see and possibly could be outside safe zones?
Regards, Matthew
Yes
TAKE ACCOUNT OF REGULATION 131.8
What about cables runs that we can't see and possibly could be outside safe zones? Not much you can do about it
Assume they are buried less than 50mm in the wall and 30 m/amp rcd them
And when you're filling out your EIC make sure that the purpose and coverage of the EIC is clear.
As des and mudock has stated plus , if you are changing the consumer unit im asuming from a fuse type to a dual RCD / RCBO board, then what you are doing is improving the safety of the installation , when this type of work is carried out you are required to completely test the installation , so what i would do is do some basic tests so faults can be identified IE shared neutrals low insulation readings etc , the other thing you must do is to install the bonding to the services gas oil water structual steel etc , the times that you should also rewire are when the installation is VIR , Lead braided paper insulated singles etc , also when the general installation is in a poor condition but initial testing should verify this also this type of work is notifiable to the LAB
Perhaps the first questions should be are you an electrician (I presume not given the way the question was asked), so please could you explain your background and where abouts in the UK are you because this will affect what Building Regs apply?