Wilko

Today attended a 70s terrace with attached garage where the owner is remodelling their utility room and want a quote to move 3 outlets and add a new one. Unfortunately the house wiring and board look original 70s kit. The board is in the garage, it looks in good shape but it's all rewireable fuses and no RCDs. The DNO side is recent TNCS, tails and bonding all good. House cabling in the garage is all neatly clipped and I'll take pics if I get the job, as I don't see this very often any more.

But I'm not feeling happy about the proposed Minor Works changes in the utility room without adding an RCD (cables in walls and the appliances in a wetish area). Your thoughts appreciated.

I could talk to owner about CU change but this will likely be a job and a half as I'm sure none of the lights will be earthed. A possible 'mare to re-wire with the family at home etc.

From left field, perhaps a new garage-type mini CU (RCD and 32A mcb) fed from existing CU and move the utility room RFC onto it? This would seem to be cheapest way to make the installation safer. I've not used this approach before and would again appreciate your thoughts and suggestions. Thanks
 
Of course you should add RCD protection in this situation for the alterations. I wouldn't be looking for ways round it either as it would likely make the job more difficult.
RCD in enclosure near the CU would be my favoured method for a small works to one circuit.

A CU update is ideal but not needed for a small job like this.
Lighting circuits post 1966 should contain cpcs.
 
Good communication with the client re further updating if needed and a good look around the house to see if CPCs are there may cadge you the work in the future. Your honesty and willingness to complete the requested minor works efficiently whilst keeping the cost down will no doubt help you in the future with this client.
Isn't there an Electrical safety council printout for clients to explain the update CU reasons, you could leave one of those for their info.
 
Is possible the existing 2.5 may incorporate 1.0 cpcs and there is a recommendation these should not be protected by BS3036, 30A fuses. Mind you this is easily rectified if it is a Wylex Standard board.
 
Wilko - I could talk to owner about CU change but this will likely be a job and a half as I'm sure none of the lights will be earthed. A possible 'mare to re-wire with the family at home etc.

Why could you not reconnect the existing lighting circuit if it had no cpc.? Aslong as there are no metal light fittings, switches or metal back boxes your improving it with mcb/rcd protection and note in comments on existing installation.
 
Why could you not reconnect the existing lighting circuit if it had no cpc.? Aslong as there are no metal light fittings, switches or metal back boxes your improving it with mcb/rcd protection and note in comments on existing installation.
Hi - thanks, I'll look into this if I get asked back. But pretty sure there were some metal light fittings :(
 
Hi - thanks, I'll look into this if I get asked back. But pretty sure there were some metal light fittings :(
Always look on the bright side of life at least you don't need to do loops, R2s and all thar stuff.
 