W
Wilko
Today attended a 70s terrace with attached garage where the owner is remodelling their utility room and want a quote to move 3 outlets and add a new one. Unfortunately the house wiring and board look original 70s kit. The board is in the garage, it looks in good shape but it's all rewireable fuses and no RCDs. The DNO side is recent TNCS, tails and bonding all good. House cabling in the garage is all neatly clipped and I'll take pics if I get the job, as I don't see this very often any more.
But I'm not feeling happy about the proposed Minor Works changes in the utility room without adding an RCD (cables in walls and the appliances in a wetish area). Your thoughts appreciated.
I could talk to owner about CU change but this will likely be a job and a half as I'm sure none of the lights will be earthed. A possible 'mare to re-wire with the family at home etc.
From left field, perhaps a new garage-type mini CU (RCD and 32A mcb) fed from existing CU and move the utility room RFC onto it? This would seem to be cheapest way to make the installation safer. I've not used this approach before and would again appreciate your thoughts and suggestions. Thanks
But I'm not feeling happy about the proposed Minor Works changes in the utility room without adding an RCD (cables in walls and the appliances in a wetish area). Your thoughts appreciated.
I could talk to owner about CU change but this will likely be a job and a half as I'm sure none of the lights will be earthed. A possible 'mare to re-wire with the family at home etc.
From left field, perhaps a new garage-type mini CU (RCD and 32A mcb) fed from existing CU and move the utility room RFC onto it? This would seem to be cheapest way to make the installation safer. I've not used this approach before and would again appreciate your thoughts and suggestions. Thanks