It is a TN-C-S system, the cutout is designed for a T-N-S or TN-C-S arrangement and is adaptable, so at some point ( probably when first installed) the DNO has taken an ELI reading and PME'd it by fitting the link. It is no different to having a TT system and appling for a PME they will only insert a link or fit a hepbond clamp on the cable and a link to the neutral. All new joints on the underground network are PME'd anyway with neutral and earth connected. If you test the ze on neutral and earth the difference is usually very small and it will tell you if the network is PME'd.