evening all, exactly as biff55 says. plus i ended up running a 16mm earth to an earth block adjacent to the lucy as opposed to joining the circuits N+E in the CEN terminal.

thanks for all the replies
 
lucy.jpgthis is the offending item in question by the way.
 
evening all, exactly as biff55 says. plus i ended up running a 16mm earth to an earth block adjacent to the lucy as opposed to joining the circuits N+E in the CEN terminal.

thanks for all the replies

Now that makes sense to me, if there is a main incoming DNO PME supply to the feeder pillar The provided earth block would be the MET for all of the feeder pillars outgoing supplies...
 