hi everyone, hope you can help. im currently installing a small submain to supply a DB which is then supplying a cctv power supply. there is a new lucy 25amp cutout in an external cabinet which has recently been installed prior to my work being carried out, when i have carried out work which involves a lucy cutout there has always been an earth block already fixed onto the side of the neutral block. The one i am working from just has concentric cable to Live and to the CEN block.
So i am asking if i require an earth rod to a new earth block, or bring an earth cable from the neutral block to an earth block? I would put a rod in myself but i just want to be 100% sure.

thanks
 
your neutral and earth are connected to the same terminal block within a pme cutout.
the smaller 25a lucy units dont have a seperate earth block.
 
What sort of overall installation are you working on?? Some sort of Highways installation??

Generally, If we are talking about a ''Submain'' from a PME/TNC-S supplied main distribution board, then you can't go making further N-E connections as you go. A PME connection is made ONCE at origin, the main distribution board should then be distributing sub-mains as TN-S, where the earth requires a separate earthing block (EMT).
 
What sort of overall installation are you working on?? Some sort of Highways installation??

Generally, If we are talking about a ''Submain'' from a PME/TNC-S supplied main distribution board, then you can't go making further N-E connections as you go. A PME connection is made ONCE at origin, the main distribution board should then be distributing sub-mains as TN-S, or TN which will require a TT earth at the load end of the distributed sub-main.
well...i thought it was clear about creating TN-C....
 

Reply to combined earth + neutral cutout in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
554
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
337
Went to a house to extend a circuit and upon doing the minor works I couldn't figure the earthing system. There was no DNO cutout and L and N came...
Replies
1
Views
767
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
565

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock