Hi there,
I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and it has 3 live fuses. I am looking to turn my house into 3 separate flats all with their own electric meter. My current WT Henley Series 8 house service cutout seems perfect because it already had 3 live fuses - however - It seems that it only has 2x neutral inputs, which is strange because surely it should have 3 neutral inputs? I know it is CNE, combined neutral and earth. It seems like it only has 2 earth inputs also.

Is there anything I can purchase so my future electrician is able to wire 3 neutral cables into the cutout? And, from what I can see on the datasheet it seems the connector block inside the neutral terminal is only rated for 100 amps? Is this correct? Because I guess it should be rated for 300 amps once all 3 live feeds are in use throughout the flats?

Thank you so much for any help,
Thomas
 
Just get a Henley block the neutral current will always be less than 100 amps, most 3 phase supplies only have 1 neutral.
Think of a 3 phase motor which may need no neutral as all 3 phases are balanced
 
  • Like
Reactions: tomsam
Firstly you need to contact your energy supplier and apply for a 3 phase supply, they will check with the local network operator to see if it is available.
Just because you have a 3 phase cutout with live fuses it doesn't mean that there is available spare capacity in the network.
The Network operator may have to do upgrades to the network.

Don't worry about the Neutral and Earths, they will be adequate assuming the supply can be used.
 
Your electrician shouldn't be doing anything to the cutout, that is the property of the electricity supplier and they make the connections to it.

You need to speak to your local DNO to arrange having the existing supply changed in to 3 supplies. If it is exactly as you have described it is likely to be a simple process of connecting one to each fuse and registering 2 new MPAN numbers
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
WT Henley Series 8 house service cutout
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
tomsam,
Last reply from
davesparks,
Replies
3
Views
1,289

Advert