Hi there, I recently had a home rewiring and the electrician spotted we had no earth. It's an old house and it was never added by previous owners.

He installed a WT Henley series 4 cutout device for the time being as it was a more cost effective solution.

He's wired it up and now the property is all grounded to this box and it has an external 100amp fuse but aside from that, I don't really know how it works and the series 4 no longer appears on the Henley website.

Do you think this is a good temporary solution?
 
Some pictures of the distribution equipment would help as it is not clear from the description what has been done

Edit: Having read your post again did the DNO install the new cutout or was it done by your electrician
 
Last edited:
Electrician did everything except change the meter which eon did
1000001491.jpg
 
I'm still trying to work out how it's all grounded, even with this cutout device.
 
Electrician did everything except change the meter which eon did
I'm still trying to work out how it's all grounded, even with this cutout device.
In fitting the new cutout your electrician has created a TNCS / PME supply which depending on the local DNO network setup may or may not be available locally
On a TNCS supply the neutral conductor is also used as the earthing conductor
 
  • Like
Reactions: DPG
I'm thinking of getting one of those mains plug wiring testers to see if it does say we're earthed. Hopefully it is all done via the neutral coming into the house as you say (have read that online elsewhere) but the wires coming into the house are quite old too.
 
Oh and yes, we've successfully avoided getting a smart meter so far!
 
I'm thinking of getting one of those mains plug wiring testers to see if it does say we're earthed. Hopefully it is all done via the neutral coming into the house as you say (have read that online elsewhere) but the wires coming into the house are quite old too.
While they may tell you that you have an earth it will not tell you how good it is
 
Normal electricians shouldn’t be touching the cutout or meter, circled in red here….

For a property to not have an earth, that’s an issue for the supplier, not for someone to invent one from thin air.

IMG_5879.jpeg

You say there’s an external fuse? Is that in a box outside? I would think the meter should be there too.
Can we see a photo of this external fuse?
 
Sorry when I said external I mean that bump on the outside of the henley. It's not hidden away inside the unit or anything. I'm not an electrician but an interested novice.
 
While they may tell you that you have an earth it will not tell you how good it is
Yeah I've been looking at this. Some martindale units seem to have the ability to give you some indication of this, which is better than one that does not I guess.
 
Normal electricians shouldn’t be touching the cutout or meter, circled in red here….

For a property to not have an earth, that’s an issue for the supplier, not for someone to invent one from thin air.

View attachment 117900

You say there’s an external fuse? Is that in a box outside? I would think the meter should be there too.
Can we see a photo of this external fuse?

The cutout box was installed by regular electrician after they said all the original sockets werent connected to any earth. the meter was installed couple of months later when eon said our spinning disc one was no longer reliable, not that I believe that, they just don't want ones that you can ubse magnets on! Still I'm happy with a dumb digital meter
 
A regular electrician has not done that head replacement just the earth terminal and do not disconnect notice suggests DNO.
 
  • Like
Reactions: snowhead
Did the electrician who joined the DNO earth with the inline connector do any Earth loop impedance tests anywhere afterwards did he not give you a Test sheet of any kind?
 
  • Like
Reactions: DPG
A regular electrician has not done that head replacement just the earth terminal and do not disconnect notice suggests DNO.
I can't make up my mind on this one whether it is a DNO swap or not as it would not be beyond a very experienced spark to do it or an ex DNO spark
 
Did the electrician who joined the DNO earth with the inline connector do any Earth loop impedance tests anywhere afterwards did he not give you a Test sheet of any kind?
I think we did get some sort of test sheet by email but I think that was just for the consumer unit box. I'll try and find it
 
It's very unlikely that an electrician replaced that cutout.

It has been carried out using DNO materials to DNO standards, the most likely explanation is that it has been carried out by the DNO
 
Last edited by a moderator:
Did the electrician who joined the DNO earth with the inline connector do any Earth loop impedance tests anywhere afterwards did he not give you a Test sheet of any kind?

cert.png
cert.png
 
Last edited by a moderator:
Certificate 2022? Test voltage 230 on IR - I'd expect that to be 250 or 500 if equipment disconnected (well that's what my MFT has).

5 Ring circuits seems mad. 7 Lighting circuits too!
 
Everything is working OK. There was lots of space in the big consumer box so had lots of circuits. Went from an old fuse wire box with 4 fuses to this giant grey box.

Got several pages but nothing specifically on if the earth is linked to the neutral from the mains, I'll have to ask the supplier I guess
 
There is a section on the mains supply which will give the type of supply as TNS, TNCS, TT etc this indicates the method of earthing
 

Similar threads

I
Replies
88
Views
15K
C

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
WT Henley series 4 cutout
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
greenruss22,
Last reply from
UNG,
Replies
21
Views
1,997

Advert