2.5mm on a 32A ocpd sounds a little bit on the non-compliant side of things.
Discuss Connection issue with swa in the UK Electrical Forum area at ElectriciansForums.net
Depending on the fixed load a 2.5mm off a 32amp mcb is no different than spurring off the ring final directly from the Mcb at the consumer unit.
If overload protection isn't required then all the 2.5mm needs is fault protection which the mcb will give.
I personally would size the mcb so Ib<In<Iz but it wouldn't necessarily be a non compliance
I hope you do realise that I'm not suggesting that it's spurred from the ring circuit, more suggested that if it was supplied from a 32 amp mcb on its own dedicated radial then as it's a fixed load it not necessarily no compliant as people are suggesting.It is different to a 2.5mm spur from a ring, this is a dedicated circuit to a single appliance and the spur from a ring is one point out of a number of points for general use. The ring circuit relies on loads being spread around the circuit to work correctly and it is advised that fixed loads greater than 2kW aren't fed via a ring circuit.
Yes you could prove by calculation that the mcb will provide fault protection for the cable, but this seems like an over the top and unnecessary thing to do for a domestic installation. Especially when you can guarantee that anyone who looks at this installation in the future will label you as a cowboy for having done it that way.
Far simpler to install an ocpd which is better matched to the load.
It will I imagine have a maximum draw if you like
If it's rated 13 amp it's not going to pull 20 is it?
why will a 13amp supply overload a 2.5mm swa?It will under an overload fault, it will not be a simple resistive load.
It wo
OkayThat is not the question I was replying to, you asked if a load rated at 13A could draw 20A, which it could under an overload fault.