You mention 'network circulating currents' in bonding cables. Is there generally current circulating in bonding conductors in PME systems then? I was under the impression that the only time current would flow in bonding conductors would be under fault conditions.
The live current has to flow in the distribution cable but some of the neutral current can divert out of the cable. This is what produces the net current. The amount of the neutral current which diverts is proportional to the impedances. Suppose the earth connection has an impedance (or resistance) 10 times bigger than the neutral current. Then 10% of the neutral current will divert and the net current is 10% of the neutral current. Now consider what happens if the neutral conductor is broken for some reason:
None of the neutral current can return in the cable so it all has to divert into the earth (or through a link box into an adjacent circuit). The net current is now 100% of the neutral current.