I would like everyone's opinion on the following.
A plastic consumer unit with full RCD protection mounted under the stairs in a semi detached house. I recently passed this installation during an EICR. It has been suggested that it should be metal due to being under the stairs. My opinion is that as long as there's no thermal damage evident then it can pass. What are your opinions on this matter?
 
I had an email exchange with one of the IET owners of the standard about this. In a non-attributable way, he suggested that such a situation should be a C3, but if not located where it could impede egress in an emergency it wouldn't be coded.
That was based on pragmatism - not immediately making thousands of newly installed CUs "dangerous" overnight.

I'd code it C3
 
Other factors to consider ...

Check terminations for tightness, especially the tails that many of us think are the cause of problems after a meter monkey's been wrangling them whikw fitting a smart meter. If there's an isolater switch, that will reduce the problem as the meter fitter won't be disturbing the CU tails.

Also, under stairs can be bare - a fire can quickly spread to the wood of the staircase. Or it might be boarded which (unless it's full of holes) will offer some resistance to fire - IIRC a single layer of plasterboard gives around 30 minutes.

And what's the layout. Does the under stairs cupboard open to a kitchen at the back of the house, away from the front door ? Or is it open plan so will very quickly impede egress ?

And a bit more tenuous, who lives there ? If everyone is healthy & fit then (assuming working smoke alarms) egress can be quick. If there's very young, very old, infirm people, then they would need more time to get out.
 