The ground doesn't have to be frozen for the whole 4' to make a considerable difference to the Ra value, which is why stability over the seasons is an important factor in any TT system....
 
Afternoon everyone, just to update the thread with regards to the job to help anyone who reads this in the future in a similar situation. I installed a 4ft rod to the outbuilding, 80 Ohms. Bonded the water. Phoned NAPIT technical support who advised me that it was acceptable to leave the CPC in the submain T&E connected, however if I wished I could disconnect it. I left it connected.

I left the existing rod in the house as I found it, tested & reconnected it to the earth bar in the new CU.

Now lets not have any bickering, enjoy the bank holiday weekend!
 
My preference would be <1Ω

So where does 80Ω come from?
Would it be that it just happens to be 80Ω on this installation and you can grab the money and run without any real work?
 
My preference is also for <1 ohm. I've done it dozens of times, my record is still the same. I've not beaten 0.29 yet. Did one last week and got 0.58 which I was pretty happy with.
 
My preference is also for <1 ohm. I've done it dozens of times, my record is still the same. I've not beaten 0.29 yet. Did one last week and got 0.58 which I was pretty happy with.

You've got the rare knack of hitting underground cables Trev! :-)
 