Have i got this right.
hob 7.2 kw, oven 4.5 kw = 59 am, with diversity, first 10 amps + 30% = 22.27 amps
Am i right this can be supplied by 6mm2 tw & e with a 30am mcb
thanks Pete
:confused:
Pete if you have a socket outlet incorporated in the control unit it is another 5 amps. I beleive a 32A mcb should be used.
What is the insallation method??
Reference method C clipped direct 6mm flat profile cable 47A capacity
Chris
Reply to cooker and hob diversity in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Hi, searched the forum but cant locate anything similar so apologies if ive missed something. Ive got a new hob to install in the kitchen...
Hello I have two new appliances Electric oven rated at 3.95 KW Induction hob rated at 7.2 KW total of 11.15 KW Currently it is on its own...
4K
Evening all, I'm upgrading my kitchen electrics replacing the current gas hob for an induction hob. The oven was previously plugged into the...
Hi all, I’m now ready to install my hob, I have a 32A MCB with 6mm T&E feeding a 50A rated switched supply at the worktop. The hob isn’t supplied...