I thought of the tripping causing inconvenience, but a double socket must be able to take over 13amps and if the toaster can only take its set load(flex protected from overload ) unless there is a short which will trip the MCB , the plug top fuse can't be there just to protect the plug . Again I know this off topic from my first question . I don't work with any other sparks so don't have these convos (extension lead unknown load I get)
The plug is under BS1363 which has the fuse requirement. So the plug and flex aren't part of BS7671 and the 433.3.1 reg doesn't apply. If you use the same flex to connect a fixed oven directly (as you are) then it's BS7671 and 433.3.1 - but I could be confused.com o_O
 
Which goes back to my first question if the flex on the hob is not fused to protect it from over current and the MCB is only there to protect the 6mm cable (take fixed V portable out of it which I accept) how is the flex protected , because we seem to think that a toaster needs to be protected from over current by a plug top fuse even though it's element pulls it rating when it's working and the flex therefore is protected and when fault happens the MCB , rcbo , RCD will trip . But if it's a oven the flex does not need to be protected from over current . If we say it to stop tripping on circuit affecting other item like a a kitchen ring then sound . But to suggest that flex on items get some new propertys just because we put a plug on them seem strange . And I know we can quote regs and bs numbers but logically does not make sense . Just a point of view not trying to be a div
 
Assuming this is a fan oven I would not consider it a fixed load because it isn't purely resistive.
 
It is a fan oven and am cool with just wiring in , RCD tested , r1 r2 sound . It just why we do it , and if the regs said we put plugs or fused spares on all other items but we let it slide on oven or hobs because it's a pain to change it and we have not had that many problems doing it this way , then fine .
( Problem solved make bigger sizefuses physical and rating which can go in to the back of the oven , flex is wired into this , fuse overloads flex protected , dragon den for me £2.50 for 80 percent of the business)
 
Assuming this is a fan oven I would not consider it a fixed load because it isn't purely resistive.
But 433.3.1 (ii) does not require a resistive or a fixed load. The qualifier is "not likely to carry overload current". I think a 10A oven on a 16A flex seems to comply?
 
If might, it's because a light bulb can't overload the light cable (got it).
If might not ?

For the oven, isn't it the same principle - sorry am I being daft again?
The chances of a cord from a ceiling rose overloading is negligible even if it is 0.5mm it will happily take 750w. I wouldn't chance this with an oven and I am not convinced this Reg is applicable.
 
Understood.
Does that mean you would only be happy with 6mm flex to match the 6mm circuit?
Edit - Personally I wouldnt use less than 2.5mm for some margin, but I'd been happy up to now that the "last metre" was ok.
 
Last edited by a moderator:
2.5 was my thinking , just to give itva bit to spare , but the connection unit at the back of the oven will not take it without bending out of shape . so 1.5 it is. The user guide say heat flex must be used as it gets very hot at the rear (I thought it cooked on the inside ). So let's hope the rubbish units it fitts in are heat resistance
 
Understood.
Does that mean you would only be happy with 6mm flex to match the 6mm circuit?
Edit - Personally I wouldnt use less than 2.5mm for some margin, but I'd been happy up to now that the "last metre" was ok.
I would change the breaker if I could not fit a larger cable but that is just me.
 