W

wrighty

hi guys

just been asked to have a look at a cooker tripping an rcd, its a split board single rcd.

she changed the element and didnt have any problems for a month. now all of a sudden the cooker is tripping the rcd after 10minutes of it been on.

any suggestions on what could be causing this, before she buys a new cooker?

cheers
 
Could still be the element (even tho fairly new), elements take a while to get to full working heat capacity and therefore can wait a little before thy trip, try an IR test on the element
 
so if thats the case would the element need changing again or what? sorry im useless with household appliances
 
sounds like another element has gone. you can IR it cold and it may show clear. with the back off the cooker, switch each element on one at a time till you find the one taheat's causing the problem. then with that element dissed, IR the bugger hot at 1000V.
 
Yeah, could be a pattern part ( cheap foreign copy) rather than original part, or just happened to be faulty outta the box, it does happen sometimes
 
Try clamping the tails with a clamp that reads mA, once it starts to warm up you will see the leakage creeping up until it trips the RCD !
 

OFFICIAL SPONSORS

Back
Top