Hi,
I've just been testing a ring final before installing an outdoor socket and I got an R1 and rn of 0.6, but instead of 1.01 for R2 I got a range of readings from 0.1 to 0.51 and it wouldn't settle down, so I couldn't continue the tests.

I know parallel paths could cause a low reading, but I've never seen an R2 reading just fluctuate wildly.

Anyone any thoughts ? Oh should add this is a new build house, only 6 months old
 
Last edited:
Hi,
I've just been testing a ring final as part of an EICR and I got an R1 and rn of 0.6, but instead of 1.01 for R2 I got a range of readings from 0.1 to 0.51 and it wouldn't settle down, so I couldn't continue the tests.

I know parallel paths could cause a low reading, but I've never seen an R2 reading just fluctuate wildly.

Anyone any thoughts ?
Was the RFC Dissed from the board completely?
 
Yes, and I'm pretty sure nothing was touching anything it shouldn't have, but fair point I'll redo the tests in the morning and double check the conductors are well away from anything
 
Mayne split the RFC at a socket also and test continuity of each half?
 
  • Like
Reactions: timhoward
Perhaps the CPCs just touching somewhere e.g. in the back of the consumer unit, or at socket where a ring has been extended out & back in, intermittent contact? Though with a new 6 month old build, these ought not to be so likely.

Or perhaps some other loose E connection giving an intermittent parallel path, e.g. a bonding connection loose. Again ought not to be so in a "quality" new build.
 
Are you mixing up your terms ? I guess you mean r1 rn and r2 to indicated loop readings on the ring , R1 & R2 for part of the earth fault loop.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
CPC low R2 continuity reading ring final
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
vwes59,
Last reply from
newfutile,
Replies
6
Views
4,831

Advert