rule number one, the meter installer should have tested for polarity
on a socket some where ,in my opinion.
on a socket some where ,in my opinion.
@Murdoch , I think you were a bit harsh on the electrician in this instance and made no comment on the incompetence of the meter installer who’s job it is solely to check polarity, fit a meter and check polarity again.
Just my opinion but. . .
Better change that cut out to a Wallaby one then ,if the All black one s are outlawed.Not only is the reverse polarity a serious meter installation fail it would appear from the only photograph shown that the cut out tails appear to be 16mm on the neutral and 25mm on the live, another fail.
All black cut outs are also reportable to the DNO as a MOCoPA C17 code as their construction materials can result in them becoming conductive leading to a detectable surface voltage being present.
I didn’t say they were “outlawed” they are just reportable under MOCoPA to the DNOBetter change that cut out to a Wallaby one then ,if the All black one s are outlawed.
In short reversed polarity is a risk to life and property.