The SWA or 2.5mm t&e would have to run through the lounge and hallway which I am not keen on doing since black SWA on the skirting is an instant no and t&e in trunking doesn’t look that nice, especially since a lot of it will be on show.If you can do that, why can't you run the new SWA in to the current CU?
It would need to be an RCD socket as this supply has no RCD protection. And no, do not put a 30mA RCD in there in place of the main switch of any new fuse-switch replacement as that is very likely to have spurious trips!
re. the MCB I meant to say RCBO

Ok, if D type MCBs take that long to trip, I won’t bother with the socket then.I doubt you would hit that unless you had several electric heaters on and trying to shower & cook. Also it takes a while to trip even at 40% overload, so really don't bother with the extra socket.