have just had a new supply installed at a job im working

supply cable in - 185mm aluminium TPN combined pen conductor split concentric cable

main fuses are 315a bs88's

supplied underground from transformer to building

does anyone have info for current carrying capacity for concentric cables?

looking at the regs this seems considerably underrated

am i missing out something?
 
185mm aluminium TPN combined pen conductor split concentric cable

cant be both ,
either protective earth neutral ( combined earth / neutral conductors )
or split con ( seperate earth / neutral conductors )

is it dno owned this cable ?
i hope so if its pen , as TNC is forbidden on the consumers side.
 
  • Like
Reactions: 1 person
cant be both ,
either protective earth neutral ( combined earth / neutral conductors )
or split con ( seperate earth / neutral conductors )

is it dno owned this cable ?
i hope so if its pen , as TNC is forbidden on the consumers side.

yes it is, they installed it, sorry its a pen conductor, not split
 
Last edited:
  • Like
Reactions: 1 person
yes it is, they installed it, sorry its a pen conductor, not split

in which case the dno will not in the slightest bit be interested in following the figures given in bs7671 to size their cable lol.
they'll be much more generous than sintras value.
;-)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Essex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Current capcacity for split concentric cable
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
Welchyboy1,
Last reply from
Guest55,
Replies
7
Views
5,590

Advert