have just had a new supply installed at a job im working

supply cable in - 185mm aluminium TPN combined pen conductor split concentric cable

main fuses are 315a bs88's

supplied underground from transformer to building

does anyone have info for current carrying capacity for concentric cables?

looking at the regs this seems considerably underrated

am i missing out something?
 
185mm aluminium TPN combined pen conductor split concentric cable

cant be both ,
either protective earth neutral ( combined earth / neutral conductors )
or split con ( seperate earth / neutral conductors )

is it dno owned this cable ?
i hope so if its pen , as TNC is forbidden on the consumers side.
 
cant be both ,
either protective earth neutral ( combined earth / neutral conductors )
or split con ( seperate earth / neutral conductors )

is it dno owned this cable ?
i hope so if its pen , as TNC is forbidden on the consumers side.

yes it is, they installed it, sorry its a pen conductor, not split
 
Last edited:

Reply to Current capcacity for split concentric cable in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top