• Please checkout this (ad-free) update post I've done on a spare blog. Feel free to bookmark it and check everynow and again for update if ads are pissing you off. Always feel free to ad-block them for now though if you want. I'll let you know when you can disable the ad blocker again, only if you want to see the ads. They should look nice and neat in the end.

Discuss DNO Concentric cable current carrying capacity in the Electrical Forum area at ElectriciansForums.net

Reaction score
0
Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he confirmed is a 25sq.mm. CNE aluminium concentric cable (1-phase, burried) for the PME supply is only able to take a 80A fuse. They will have to dig in a new supply cable (presumeably 35sq.mm) to complete the upgrade to 100A. The supply isn't looped and the meter/consumer tails have already been upgraded to 25sq.mm. so no problems there.

It seems strange to me that they say that this cable isn't able to take 100A? Looking at datasheet from Cleveland it looks like worst case is CCC of 105A.
Was the guy correct to say that 80A fuse is the max on that cable? Obviously it's at their expense to dig in the new cable but it would be much better to avoid the hassle of it all if it's not needed. I have a link to a UKPN document EDS 02-0033 which documents the current carrying capacity of some larger waveform cables from 95-300sqmm but can't find anything for domestic supply 25sqmm cable.
 

OnlQQker

Esteemed
Reaction score
1,245
When I was studying 12 volt high amp cables, the rule of thumb was to leave at least 20% of the cable bigger than the ampage itself after all factors had been taken into account. I times that amount by 4 on the battery cables themselves.

Perhaps they're doing the same thing now?
 

Marvo

-
Staff member
Mod
Mentor
Esteemed
Supporter
Reaction score
10,107
If it's an aluminium concentric wavecon type cable it's quite possible it's not rated to be buried unless it's ducted...
 

R-fur

-
Esteemed
Arms
Reaction score
680
If it's an aluminium concentric wavecon type cable it's quite possible it's not rated to be buried unless it's ducted...
It sounds like a straight concentric cable which will have a 25mm solid aluminium core surrounded with copper wires for the CNE. Quite common in the UK.
Aluminium wavecon cable was used by some UK DNOs and was rated for direct burial.
 
OP
S
Reaction score
0
Not sure if it is buried direct or ducted. I guess they would ducting them as a standard practice? (At least these days. Who knows what they were doing in 1980 when these houses were built).

Again, not sure if it's staight or wavecon. The guy who came said wavecon (or waveform he call it) but they wouldn't be tapping off that section so it could easily be straight.

Any ideas what CCC UKPN or other DNO's allow, and in terms of fusing whether 100A or 80A max.? I have heard that similar houses on the same road, built at the same time, were upgraded to 100A without needing change the cable.
 

Rockingit

-
Mentor
Esteemed
Arms
Supporter
Reaction score
5,922
Could it be because the cs of the Neutral spiral is 50% of live conductor? If so, I believe they're trying to uprade most networks to be 1:1. Just a thought.
 

R-fur

-
Esteemed
Arms
Reaction score
680
A 25mm Al conductor should be able to carry about 120A so a 100A fuse should be ok.
Waveform or wavecon cables are used as distributors not service cable. I don't think I have ever soon a waveform cable smaller than 70mm.
Ducting is not standard practice for distributor cables as it derates them by 30% and makes it difficult to joint services onto them.
The service cable to your place is I believe single phase so the neutral will be fully current rated, although as it could be copper it may be physicaly smaller.
 

Reply to DNO Concentric cable current carrying capacity in the Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
405
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
946
Did an EICR that passed 5 years ago Several things in the picture raised concerns for me. Comments please - photo at end First photo shows a...
Replies
9
Views
860
Hi Guys Any one know the current carrying capacity of a 4mm 3 core single phase sy cable ran in a 20mm pvc conduit? Not sure of the right table...
Replies
2
Views
626
Got an EV (Nissan Townstar EV) in my house, has a Zappi EV charger installed (by myself) and notified via ENA form to Scottish Power energy...
Replies
4
Views
765
Advertise Here

New Posts (Please Reply)

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top