Did an EICR that passed 5 years ago
Several things in the picture raised concerns for me.
Comments please - photo at end

First photo shows a split concentric in use AFTER the meter, the supply is a TNC-S supply and the split concentric has the following items
  • Single insulated neutral conductors that are accessible to touch C2
  • Unsleeved cpc on the split concentric C2
  • Single insulated line conductor- this is thicker than normal and may be aluminium (have put this down as FI)
  • Split concentric cable has neutral and earth wrapped around the inner line conductor and appears therefore to have neutral conductors acting as a armour in case of a fault listed as FI
20230503_094606.jpg


Second photo

Gas meter (plastic incoming pipe) has copper outgoing pipe which goes underground and can induce


20230503_094629-2.jpg
 
After the meter isn't an issue in itself.
What is the route of the split-con? Does it stay above ground and is it visible and surface clipped once inside as it goes to the CU?
As well as the obvious single insulated issue I'm thinking about lack of over-current protection and whether it in fact needs RCD protection. And the lack of mechanical restraint of any nature.

The gas is definitely extraneous, I guess there's no bond inside where it enters?
 
After the meter isn't an issue in itself.
What is the route of the split-con? Does it stay above ground and is it visible and surface clipped once inside as it goes to the CU?
As well as the obvious single insulated issue I'm thinking about lack of over-current protection and whether it in fact needs RCD protection. And the lack of mechanical restraint of any nature.

The gas is definitely extraneous, I guess there's no bond inside where it enters?
Cable goes under floor (I think it is concrete) and rises at consumer unit under stairs
It is inside brick cavity at the meter box and goes down.
There was no adequate continuity on the gas pipe work (0.11 ohms)
 
Not sure about the FI for basic insulation exposed to touch. I would say that's a C2, no investigation necessary.

Unsleeved CPC would not warrant a code at all in my opinion, maybe just a comment. Unless there are two different earthing systems present that can be touched simultaneously, then it would be C2.

About the neutral and earth conductors wrapped around the centre line conductor, that's just how split concentric cable is constructed. It is not an armoured cable, and therefore cannot be used to satisfy the requirements for safe zones, and would probably need 30mA RCD up stream, depending on the installation route.
 
Split-con....... so, here's one for debate: This is all inside a locked cupboard that requires a 'tool' (mbox key) to open.
 
Split-con....... so, here's one for debate: This is all inside a locked cupboard that requires a 'tool' (mbox key) to open.
This argument has been raised before. My reply is that the customer, classed as a normal person, or even their child at the request of the parent, will be regularly opening the door to read the meter, and in this case to top up the meter. In my view, common sense would override that particular regulation.
Add to that the number of damaged doors that cannot be locked that we come across.
 
Is concentric not classed as reinforced insulation? ie, not basic insulation
Not the centre core connected to L as exposed here. When used by the DNO it all is enclosed in the cut-out.

It is in my mind fairly safe in the sense that a penetration by nail etc, has to go through at least N or E but of course N cannot be considered "safe" in the general sense as it is one of the live conductors. Of course DNO treat it as safe to bury, but that is no longer consider enough under BS regs.

As already mentioned it is probably not under the '3m rule' for fault protection.
 

Reply to Split concentric after meter, queries in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi everyone, I need some help with an electrical issue I'm experiencing. I recently created a new circuit for an electric oven at my friend's...
Replies
7
Views
2K
Hello everyone, I’m based in the ROI and live in a rural location. Yesterday evening my electricity supply started to switch on and off randomly...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock