A

A.foster

Hi looking for some advice I am about to start a commercial job in a rural area the venue is being totally renovated it is a 30 bed hotel which is being extended will have 2 bars large function room a large commercial kitchen and a spectate motel in the future. The venue is only supplied on 2 phases only To upgrade to 3 phases they local sub station will have to be upgraded and a new line dug to venue. The custerner Is wanting to install air con units which will take up a lot of demand I have recommended to not go with air con and gas appliences in the kitchen. Has anybody come across this problem before? And does anyone have any possible solutions? Thanks
 
Tell your client to apply to the energy supplier to have an adequate 3 phase supply installed. The supply characteristics should have been discussed at the planning stage of a project like this not left until the last minute. IMO
 
As above, it would seem like this whole project could anchor on the supply available and it should never have left the table until a solution had been found, I suspect a DNO TX plus cabling could be anything from 20k - 100k situe dependent and they may request part of the land to house the TX and all rights to access (again situations vary).

If your customer seems to be turning a deaf ear then you need to arrange a meeting with the building contractor and all parties affected, this could mean some large contracts are stopped on the site which too could have legal fallback.

The customer 'if unaware' of this at the planning stage will be perfectly within their rights to demand some explanation and possible compensation if the project is delayed or major costings and/or changes are made to the contract.
 
I would also check and see if it is in fact single phase 3 wire. Often in rural areas you find this on older installations.

It may very well be 2 phases, but unusual for a DNO to unbalance things like that

Agree with above suspect it will be split phase (3 wire single phase) Its easy to check as the sum of the 2 phases to neutral will equal the voltage across the lines (phases) ie 230v +230v = 460v if it was 2 poly phases it would of course be 400v and 230 between line and neutral.
Voltages shown for comparison actual will be more.

The convertors benji mentions are an option you just need to find the size of the supply and check its adequate.
 
Last edited by a moderator:
Specialist transformers may be a solution - something like a Scott-T which can convert the 2 phase to 3 phase. If your existing 2 phase supply is sufficient then you should be able to get VSD driven AC units which will run quite happily with a 2 phase supply to them, yet provide the 3ph required for the compressors and fans. The AC will be more expensive than conventional, but there will in the longer term be savings on the compressors and fans due tou this.

If the loading on the supply is going to increase significantly then that needs to be cleared with the DNO also, and to verify that the existing cabling us adequate.
 
Agree with above suspect it will be split phase (3 wire single phase) Its easy to check as the sum of the 2 phases to neutral will equal the voltage across the lines (phases) ie 230v +230v = 460v if it was 2 poly phases it would of course be 400v and 230 between line and neutral.
Voltages shown for comparison actual will be more.
This was my first thought when I saw the word 'rural' and 'two phases' in the OP. Before going any further check the voltage between the two phases, if it's 480V this will add to your design issues.
 
what sizes are the main fuses and cable?100 amp mightnt do. you could maybe get a larger cable put in,albeit 2 phase without the cost of changing the substation......or get some eco **** put in..wind mill solar panels,ground source heat pump....wood chip generator
 

Reply to currently 2 phases in venue unable to upgrade to 3 phases in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
511
Hi, we are converting old farm buildings to commercial units, and as my father used to run a vacuum pump and compressor in his dairy I always...
Replies
13
Views
2K
Hi I have UPS 50KVA and the inverter output AC voltage is feeding a distribution panel 120/208 V 4 wires when I check UPS display it shows me...
Replies
1
Views
237
Hi I have a question hoping I can get some help. I wanted to know if there is a 400V 3 phase supply (A/A/A) terminated on the primary side of a...
Replies
3
Views
831
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock