The pictures look wrong and this all sounds wrong ask the land lord for the last EICR Or PIR and unplug those extension leads before the place burns down !!!!
 
I get the impression the OP doesn't want to listen so I'm unsure why he asked in the first place TBH.
 
Do you have access to a main switch to isolate in the event of an emergency ?

If the DNO fuse counts, then yes.

I get the impression the OP doesn't want to listen so I'm unsure why he asked in the first place TBH.

I'm more concerned about having the RCD trip or whatever, than overloading the 10A fuse in the socket. The cable near the plug has been shortened for anyone who is concerned, so it's not looped anymore :D
 
The RCD will trip if there is high earth leakage but if you are not concerned about over load then I am concerned ! Overload causes fire !! every time you add an extra extension lead the resistance is getting higher due to the connection between plugs and sockets and the length of cable Resistance means more heat more heat means fire !!!
 
Resu

and many other unansweable questions like

why would someone blow them selves up on a bus.

because there are a rich tapestry of people in the world? (My diplomatic answer)
 
The RCD will trip if there is high earth leakage but if you are not concerned about over load then I am concerned ! Overload causes fire !! every time you add an extra extension lead the resistance is getting higher due to the connection between plugs and sockets and the length of cable Resistance means more heat more heat means fire !!!

Sorry I may be having a blond moment but assuming the lead that is plugged into the supply socket is fused appropriately for all cables in the daisy chain (eg 13A rated all of them) then how can there be an overload risk? (I am assuming all unwound fully)
To me the issues are:
Disconnection times under fault (increased Zs value)
Volt drop
A serious effing trip hazard lol
 