Hi all,

I have an engineer who has failed a wall mounted data cabinet because the PDU is hard wired into a switched fused spur, the spur is spurred off a ring main in 2.5/1.5 twin and earth.

He has failed it under regulation: 543.7.203 The wiring of every final circuit and distribution circuit intended to supply one or more items of equipment, such that the total protective conductor current is likely to exceed 10 mA, shall have a high integrity protective connection complying with one or more of the following:
(ii) A single copper protective conductor having a cross -sectional area of not less than 4mm, complying with the requirements of regulation 543.2 and 543.3, the protective conductor being enclosed to provide additional protection against mechanical damage, for example, within a flexible conduit.

My question is, how can you determine the protective conductor current of a piece of equipment? This is a wall mounted cabinet with a few switches in it, no servers pulling high amounts of power and I doubt the cabinet as a whole is exceeding 3.5 mA (Reg 543.7.201) let a lone 10 mA. Unfortunately I am not signing my name to the test results and I need to make sure we're doing things properly.
 
Hi all,

I have an engineer who has failed a wall mounted data cabinet because the PDU is hard wired into a switched fused spur, the spur is spurred off a ring main in 2.5/1.5 twin and earth.

He has failed it under regulation: 543.7.203 The wiring of every final circuit and distribution circuit intended to supply one or more items of equipment, such that the total protective conductor current is likely to exceed 10 mA, shall have a high integrity protective connection complying with one or more of the following:
(ii) A single copper protective conductor having a cross -sectional area of not less than 4mm, complying with the requirements of regulation 543.2 and 543.3, the protective conductor being enclosed to provide additional protection against mechanical damage, for example, within a flexible conduit.

My question is, how can you determine the protective conductor current of a piece of equipment? This is a wall mounted cabinet with a few switches in it, no servers pulling high amounts of power and I doubt the cabinet as a whole is exceeding 3.5 mA (Reg 543.7.201) let a lone 10 mA. Unfortunately I am not signing my name to the test results and I need to make sure we're doing things properly.
You need an Earth Leakage Clamp Ammeter, (not a cheap item)
 
Hi all,

I have an engineer who has failed a wall mounted data cabinet because the PDU is hard wired into a switched fused spur, the spur is spurred off a ring main in 2.5/1.5 twin and earth.

He has failed it under regulation: 543.7.203 The wiring of every final circuit and distribution circuit intended to supply one or more items of equipment, such that the total protective conductor current is likely to exceed 10 mA, shall have a high integrity protective connection complying with one or more of the following:
(ii) A single copper protective conductor having a cross -sectional area of not less than 4mm, complying with the requirements of regulation 543.2 and 543.3, the protective conductor being enclosed to provide additional protection against mechanical damage, for example, within a flexible conduit.

My question is, how can you determine the protective conductor current of a piece of equipment? This is a wall mounted cabinet with a few switches in it, no servers pulling high amounts of power and I doubt the cabinet as a whole is exceeding 3.5 mA (Reg 543.7.201) let a lone 10 mA. Unfortunately I am not signing my name to the test results and I need to make sure we're doing things properly.
Ben does the item of equipment have an details as to the predicted earth leakage? I take it from your post that the Ring Final Circuit RFC has not been wired as per regulation 543.7.2.201 pagev87 On Site Guide 18th Edition
 
Thank you for the replies, I misunderstood the whole picture of the failure and focused solely on this problem, I am human and still learning the vast information the BS hold! Next question is how do I remove a post so I don't get bombarded with replies?
 

Reply to Defining what equipment has protective conductor current in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
All - Would appreciate some advise or professional help as I'm facing a £4.5K bill following an EICR which seems to highlight issues that passed...
Replies
21
Views
4K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Hi! I'm willing to build up a network within my residential house which includes outdoor equipment for WAN access. And I'm failing to figure out...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock