Hi, I’m interested to hear other views on BS3871 MCBs being changed following a C2 non compliance on an EICR for over rated protective device. Eg. A 2.5mm radial circuit protected by a 32A device and then swapping the BS3871 for another BS 3871 but a 20A device.
 
What make/type is the board?
 
Ref method A 20 amps
Ref method C 27 amps
So yes I’d agree to downgrade the 32A. What to depends on the Ref method.
 
What is the cable supplying?
It may be ok as it is.
 
  • Like
Reactions: Bsharp
What is the cable supplying?
It may be ok as it is.
I suppose if it was supplying a fixed rate piece of equipment (I.e. less than 27 amps with correct install
methods and seating factors applied) you could say it’s “ok”
 
I suppose if it was supplying a fixed rate piece of equipment (I.e. less than 27 amps with correct install
methods and seating factors applied) you could say it’s “ok”
More information is required really such as length, installation method and what it's supplying.
 
If it is a fixed load of 20A-ish or less it might be fine, subject to end of circuit Zs being able to meed ADS time.

Otherwise (e.g. socket outlets so unknown load profile) it ought to be down rated to 20A or 25A depending on the method(s) along the length of the cable.
 
So starting from the top.
I’m looking for general thoughts rather than a particular installation. But to keep it simple I’ll use an example I’ve come across. MEM 32A Type C feeding a radial socket outlets, singles in trunking and conduit with flush floor box. Located in a public area of a shopping center for pop up traders to use. A direct and approved MCB is not available in a 60898 or RCBO to 61009. Old stock 3871 are available from national wholesaler, but would you agree that fitting this then changes the design of the circuit ? My question is if available would you or would you not fit ?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
South Wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Heavily Qualified Electrician / Teacher / Tutor - etc

Thread Information

Title
Derating a BS3871 following an EICR C2
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
CalHD29,
Last reply from
davesparks,
Replies
9
Views
1,104

Advert