Leesparkykent
[PDF]Design Range of Consumer Units - Hager
www.hager.co.uk/files/download/0/12240_1/0/ConsumerUnit.pdf
Guidance from BEAMA (British Electrotechnical and Allied Manufacturers Association) who represent the UK ... minimise flames from escaping a consumer unit in the event of a fire. ... Annex ZB. ...... and (Annex ZA 16kA conditional).
look at the label in then DB page 10 lol! But I do like the cable clamp for the tails entering the main switch page 11.
It does look as if Hager have actually listened to electricians when designing these boards. I wonder if the figures will stack up. Saying that Hager have always been competitive.
Is there any mention of square grommets to fit the holes , and are these holes to be sealed once the cables installed , I like the clamp arrangement , would also be good if they supplied a db schedule that sticks to the inside of the door ...
Use grommet strip on the square holes
Why would the holes around the cables need to be sealed?
Exactly. The distribution board only need to be made from non-combustable material. So, it won't in itself catch fire. If it does not catch fire it won't matter about the holes as it will self-extinguish.
Not sure if this amendment 3 would also mean sealing the void around the cable entries , i.e. in the rear knockouts , also grommet strip is o/k on the larger oval holes in rear but for it to stay in place on the square knock outs is something else , a grommet pack supplied would be better
They will require no more sealing than they do under the current version
With the grommet pack in mind these could be blind and would help in both respects , also its a bit pointless making a M/C board to contain any possibility of a fire with such a large rear knockout IMHO, again large oval blind grommets to fit the holes would at least help in some way...
And then mount the DB on a bit of chipboard also lol
Who's making metal boards to contain fire? It's certainly not required under ammendment 3, that merely requires the board to be manufactured from a non combustible material not that it forms a fire sealed enclosure or anything like that
1. What is a definition of non-combustible?
There is no published definition for ‘non-combustible’ that aligns with the intent of regulation 421.1.201. Ferrous metal is deemed to be one example of a non-combustible material that meets the intent of the regulation.
2. What constitutes a ‘non-combustible enclosure’?
A non-combustible enclosure includes base, cover, door and any components e.g. hinges, covers, screws and catches, necessary to maintain fire containment. See diagram 1. Blanks and devices are contained within the non-combustible enclosure.
and as for cable entry's.
3. How is account taken of cable entries into a ‘non-combustible enclosure’ with respect to containment of internal fire and escape of flames?
Good workmanship and proper materials must be applied by the installer. The cable installation entry method shall, as far as is reasonably practicable, maintain the fire containment of the enclosure. Account shall be taken of the manufacturers instructions, if any.
Non-combustible material” means material that does not burn or give off flammable vapours in sufficient quantity for self- ignition when heated to 750°C
I can see different manufacturers will have their own interpretations and supply what they think is right , I heard the mention of wiska glands being used by some , I and others will just see what happens when it comes to it ...
Care to cite your references for that? Is it something the IET has published or is it a third party's interpretation/opinion?
The new amendment mentions nothing about cable entries into distribution boards over what has already been in previous versions of BS7671.
I like the look of the Hagar boards.
I do believe they come with grommet strips (could be wrong).
They are made to be able to use different size trunking with the knock outs so that satisfies the IP issues and as said previously there is no provision needed to make the entries "fire sealed" as this is not mentioned in the new regulations.
Leesparky states the Beema reference which makes it clear what needs to be made and installed.
Also the cable clamps only come with the 30 version I think (could be wrong again) but sure it could be used in the 10 version.
The tails kit are great, used them for ages but it looks like they will not be used in the new boards.
I really don't think they are going to change the meaning of English words though.
Is is this better from the Oxford dictionary:
Made of material that does not burn if exposed to fire; incombustible.
That's no specific enough for this application of the phrase, the temperature the material is going to be exposed to needs to be defined.
Steel will burn if exposed to fire of sufficient temperature,