kudruvaki
Hi
Recently got a stove from the USA
This is the Info
3 wire - 1 phase - 60Hz - A.C only
For use on 3wire - 120/240 or 120/208 v. system
120/240v
12.6KW
120/208v
9.5KW
For use in Fiji according to our electrician, he cannot guarantee if its safe or not the detail below is our power supply in Fiji
3 wire - 1 phase 50Hz - a.C Only
there is a difference of 10 hz
how safe is it?
Any suggestion or recommendations
:confused::confused::confused:
Hi
This is the Info
120/240v
12.6KW
120/208v
9.5KW
how safe is it?
Hi,
You haven't mentioned what voltage you have there at your premesis
in fiji. But as for your frequency difference,it should only effect your clock{if you have one}.Your carefully timed curry may be a little burnt,but there should be no other safety issues provided your electrician connects up correctly.If as I think is the case your voltage is 230volts(+or- 10volt)It is likely that your american cooker cable colours are green for earth,white ,neutral,red hot1,black hot2.The usa voltage gives between neutral and hot1 120v,neutral and hot2 120v,hot1 and hot2 240v.So for your supply voltage you have 230v between neutral and hot(live).this would need to be connected to your hot1 and hot2 on the cooker.The cooker white neutral would then not be used.Hopefully your control circuit,clock and indicater lights are 230volt.or else your spark may have to do more internal alterations.:rolleyes:
Thanks for that.
our Power in Fiji -Voltage: 220-240 Volts
Its just that the oven uses - Precision Cooking™ System with Precise Preheat
Precise Preheat will alert you based on actual temperature, not a preset time, for more accuracy and better results.
difference in Hz different country {filename} | ElectriciansForums.net
Thanks for that.
I recon you would be best trying to contact the technical support of your stove's manufactor.Perhaps a240/110 transformer could be used if you needed dual voltage.I still however don't think the frequency (Hz) will be a problem.Good luck.
Reply to difference in Hz different country in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net