I’ve never heard that one but you are obviously more learned in that sort of thing than meHmm I've heard this is quite common in your area of Cornwall.![]()
.High heel DeWalt boots maybe

I’ve never heard that one but you are obviously more learned in that sort of thing than meHmm I've heard this is quite common in your area of Cornwall.![]()
.
Kirsty in a dress, she doesn't normally wear a dress!I asked this question of an SPD manufacturer (Surge Devices) at a trade fair. They said exactly what you said.
Random thought, but did you spend a day in Manchester wearing a dress about a year ago?

The bells, they made me deaf you knowExactly the same thing, except that it could be argued that a bell Tx radiates a magnetic field that could conceivably affect RCDs on the board.

Is this one you’ve installed? If so and you’re questioning it, why not swap it for the same brand as the DB and then you’re covered?Is there a reg anywhere that states that you have to use the same make SPD inside a consumer unit. I know there are with MCB's as they obviously have to sit on the same bus bar but an SPD just slots in and has flexible cables wiring it up.
Because it's fine as it is. Why should he back down just because some 'council bod' doesn't know his job?Is this one you’ve installed? If so and you’re questioning it, why not swap it for the same brand as the DB and then you’re covered?
Because it's fine as it is. Why should he back down just because some 'council bod' doesn't know his job?
Because it's easier and cheaper to go along with what the muppet wants than it is to stand your ground and potentially lose a lot of future work for that council.
I completely agree that you shouldn't have to back down and change an installation because someone else doesn't know the rules. But at the same time landlords don't accept principles in liue of money when it comes to paying your rent.
Like Davesparks says sometimes it’s easier to just change something and rid yourself of the potential headache of all the other implications that come with standing your ground.Because it's fine as it is. Why should he back down just because some 'council bod' doesn't know his job?
However, it is true that the regs do say that for a domestic installation, we must use a type tested CU. If we include anything in that CU that is not part of the manufacturer's type testing/acceptance, then we have invalidated it. So technically, putting anything other than the manufacturer's own bits (or bits they specifically approve) into it means we don't comply with that particular rule.
The only reason this clause has been included in BS7671 is that electricians were ignoring the requirements of the legislation and the other relevant standards with which they should have been complying.
The requirement for using all the same make devices has been in place in the relevant applicable standard since 1991, in round figures 32 years.
For most of those 32 years, sparks ignored the requirements.
Therefore, compliance with the standards listed therein is compulsory for compliance with BS7671.
The standards are listed in BS7671 and available to buy from BSI, they always have been.I wouldnt say ignored, the vast majority of electricians don't even know those standards exist, and for those that do there is no ready access to them.
Not being aware of something's existence is not the same as ignoring it.
If we are expected to know these standards and how they apply to our work why aren't they made readily available to us?
But until we get reasonable access to those standards and this gets included in formal training for electricians how are we going to have a cat in hells chance of complying?