Discuss Different sized csa cables on same circuit in the UK Electrical Forum area at ElectriciansForums.net
Gavin John Hyde
Patron
Got a house I am working in at moment, customer wants extra sockets downstairs, apart from kitchen the whole ground floor has just 3 double sockets.
The current sockets in the lounge/diner are fed by a 6mm twin and earth( from old cooker circuit that was rerouted when a gas cooker went in) and tests out fine with great IR Readings. From this is a spur in 2.5/1/.5 to the next 2 sockets. It is currently also protected by a 32 amp MCB, fine for the 6mm but not for the 2.5mm so will be downrating the MCB as part of the work to make a compliant radial.
Will use this 6mm feed to supply the new sockets I install as it saves ripping up the lovely wooden floor in the hallway.
What size would you put on the certificate? 6mm or 2.5mm? personally I think the lowest sized cable with a note explaining the different sizes? as it has the lower capacity.
What is every body else doing in this scenario?
Reply to Different sized csa cables on same circuit in the UK Electrical Forum area at ElectriciansForums.net
Came across a cooker circuit with 10mm and 40A rcbo. Last leg was 6mm. Isolator to outlet. I downgraded to rcbo to 32A to accommodate the 6mm...
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...