Gavin John Hyde
Patron
Jun 4, 2017
3,811
5,857
3,541,381
Somerset
www.sulis-electrical.co.uk
Business Name
Sulis Electrical Services Ltd
Got a house I am working in at moment, customer wants extra sockets downstairs, apart from kitchen the whole ground floor has just 3 double sockets.
The current sockets in the lounge/diner are fed by a 6mm twin and earth( from old cooker circuit that was rerouted when a gas cooker went in) and tests out fine with great IR Readings. From this is a spur in 2.5/1/.5 to the next 2 sockets. It is currently also protected by a 32 amp MCB, fine for the 6mm but not for the 2.5mm so will be downrating the MCB as part of the work to make a compliant radial.
Will use this 6mm feed to supply the new sockets I install as it saves ripping up the lovely wooden floor in the hallway.
What size would you put on the certificate? 6mm or 2.5mm? personally I think the lowest sized cable with a note explaining the different sizes? as it has the lower capacity.
What is every body else doing in this scenario?
I would probably opt for "6 / 2.5" (with an explanatory note as appropriate).
Ooh are you doing a lollipop?
No lollipop as I have always thought a lollipop would be a 2 legs of a ring coming off a larger single cable that feeds them both.
Gavin John Hyde
Patron
Somerset
Website
http://www.sulis-electrical.co.uk
Business Name
Different sized csa cables on same circuit
Gavin John Hyde,
GBDamo,